We have a mezzanine floor within a warehouse that will support heavy racking loads, which will be operated by a robotic system. The robotics supplier has specified a stringent deflection criteria, requiring that the floor deflection not exceed 10mm at any point.
Okay. That is now more clear.
Our structural analysis software indicates a global deflection of 10mm
What does this mean? Is that the deflection of the non-composite (i.e. naked) steel beam under non-composite loads? Because, that deflection doesn't really matter.
Is it the 10mm deflection of the composite beam under loading that is applied AFTER the beam has achieved it's composite stiffness / strength?
It is VERY important that you understand what this deflection is and when each component of the deflection occurs. Only then can you understand how it impacts your client's design criteria.
My interpretation of your clients design criteria:
1) The robotics manufacturer cares about having a FLAT floor. Where that floor can't have any more than 10mm of variation in flatness. But, I don't think they care at all how you got there... Honestly, that's not all that a terribly strict flatness criteria.
2) Typically, whether the mill camber is up or down does not AT ALL affect whether the top surface of the slab is flat! Please try to understand this.
The slab is poured so that the top surface is flat within some construction tolerance. Gravity pretty much makes this happen since the concrete is reasonably fluid while it is being poured.
Any deflection that happens before they are finished pouring the slab will be totally irrelevant to the robotics folks.
Why? Because the robotic equipment has no idea that deflection ever occurred and will never be affected by it.
3) What the robots guy cares about is any load applied AFTER the slab has become composite. Meaning dead loads applied AFTER the slab was poured. Live loads including the weight of whatever robotic equipment is running around.
To ensure a minimum 200mm thick concrete slab, we must orient the beam with a downward camber, making an upward camber impossible. Our structural analysis software indicates a global deflection of 10mm. Considering the fabrication tolerances, I explained that an additional 6mm deflection should be accounted for, resulting in a total deflection of 16mm.
Why do you think it matters if there is a maximum of 6mm various in slab thickness?
First off, I'll suggest that much of this camber will flatten out when the concrete is poured if the camber is oriented upwards. Generally speaking, when you design a composite beam system you will try to specify a camber which is on the order of 70 or 80% of the pre-composite dead loads. In your case, you have rightly determined that cambering the beam is not economical since it is so short. That's fine. But, you still generally want to orient the natural mill camber upwards so that the beam flattens out under the weight of the slab.
This are concepts that should be familiar to anyone who understands the basics of composite beam designt. The fact that you don't seem to understand this is, to be frank, a bit of a red flag to me (and probably most experienced engineers reading this thread). I'm really hoping that that you're not the engineer of record for this project... and that there is a more experienced engineer in your office that can explain this to you.
Sorry to be so blunt about this. Perhaps there is a bit of a language barrier here that is causing the misunderstanding. Your English is actually pretty good, so my comments have presumed that this is NOT the case.