Agree totally with LittleInch, if there is a slam shut valve at the tank, they can be very problematic. Everything happening there reflects back to hit the meters. I would question the need for such quick action downstream of the meters at an onshore tank farm. Tanks should have hi & hi hi level alarms and sufficient freeboard above those so as to not make them necessary for overflow control, so what makes a snap acting valve necessary there? The tanks not shoving off a bouy, or going anywhere else and they are usually just watched closely and let to burn themselves out over several days even if they catch fire. A couple hundred barrels more in the tank wont make much difference. Slow those down. Snap acting ESD valves should be located upstream of the meters and PCV unit where there is more HP pipe upstream to contain full surge pressure. Put the surge control skid (if needed) inbetween the ESD and a HP PCV, which tends to keep most surge pressures directed upstream and/or moving into the surge skid as it closes, then the meters and lastly the backpressure controller. Even so you still may need the surge skid. I have designed many pretty high flow product and crude pipelines and that arrangement always works, sometimes without a surge skid, and even with a snap valve at the tank, but I did manage to keep station velocities lower than you did.