Is CYMgrd or ETAP able to model the interconnection of a solar PV farm earthing grid interconnected with its interconnect substation earthing grid?
The issue is that when injecting the short-circuit currents from the substation into the earthing grid of the PV plant, it does not support it, because there will be no faults of the magnitude of the faults in the substation in the PV zone.
That is: Is it possible to simulate faults differentiated by zone? and evaluate the effect of short circuit in the substation (high fault values) on the PV zone (very large area with weak phase-to-ground short-circuit currents).
The issue is that when injecting the short-circuit currents from the substation into the earthing grid of the PV plant, it does not support it, because there will be no faults of the magnitude of the faults in the substation in the PV zone.
That is: Is it possible to simulate faults differentiated by zone? and evaluate the effect of short circuit in the substation (high fault values) on the PV zone (very large area with weak phase-to-ground short-circuit currents).