Dear Experts,

i want to know the way of contactor sizing of dahlander motor. the motor is variable torque type.
thanks in advance.
 
Replies continue below

Recommended for you

Size the contactors according to the current which will flow in them. If the contactors are IEC types then the AC-3 rating is the one to use, unless you're doing something more severe like inching or plugging which would take it to the AC-4 or AC-5 rating.

Hint: the low speed contactor is sometimes smaller than the high speed and shorting contactors, which are normally of equal rating.
 