I have a 30hp 480V Siemens MM440 VFD that recently failed. When pulling the VFD out of service to investigate, it was obvious that something has been smoked for there was black soot all over the enclosure and the control boards.
Upon taking all the boards apart and looking at them one by one we found that it appeared that only two of the capacitors were all that were damaged. These capacitors appeared to be burnt up and was obvious that they were the cause of the failure. Everything else seemed to be fine, and it appeared that these capicitors smoking were the cause of the soot elsewhere.
What would cause capacitors to fail suddenly like this? Is it possible that they were subject to overvoltage? What is the common cause of capacitor damage in VFD's?
I should mention that this VFD is on a HRG system limited to 5A.
We have suspected possible voltage transients in this area for a while. In some cases overnight when the VFD was not in use the drive would trip out on a DC bus overvoltage. This led us to belive that there were some transenits occuring in the system subjuecting the DC bus to overvoltage.
I'm going to put a fluke 1735 power meter down in the area to monitor voltge. The meter will only pick up events lasting for 1/2 cycle or more. Do you think the meter would pick up a voltage transient or are typical voltage transients shorter than 1/2 cycle?