Mechanical
- Oct 6, 2005
- 45
Hello All,
I was trying to figure out the amount (CFM) of outside air leaking through a closed control damper. After some thought it seems the best method is to calcualte the outside air percentage based on temperatures per the following:
x% = outside air percentage (OA%)
Ta = outside air temp
Tb = return air temp
Tc = mixed air temp
x% = (Tc - Tb)/(Ta - Tb)
If I know the total CFM, then multiply total CFM by OA% to get the air leaking through the damper.
I appreciate any thoughts...