simpeltech
Electrical
- Jan 14, 2010
- 1
I am having a discussion on damper sizing and it came down to which factor to use for calculating the required torque for a damper. Now, I proposed the use of the following will more than suffice:
1. For opposed blade actuators with seals is ~5 in-lb/sq.ft.
2. Torque Loading multiplier of 1.5 for fpm of 2000 to 3000 fpm.
3. So 7.5* X sq.ft. = Total torque required(in-lbs)
So, I was told to use 14 in-lb/sq.ft. for a 40+ year old OA damper that is 30.38 sq.ft and 888 fpm. Does that sound right to anyone? Is my information above bad? My logic is that at the actuator will be oversized to overcome a lack maintainance on the damper. And also, will oversizing have a negative effect on a dampers' mechanical operation?
Thanks to everyone ahead of time for your help and time.
1. For opposed blade actuators with seals is ~5 in-lb/sq.ft.
2. Torque Loading multiplier of 1.5 for fpm of 2000 to 3000 fpm.
3. So 7.5* X sq.ft. = Total torque required(in-lbs)
So, I was told to use 14 in-lb/sq.ft. for a 40+ year old OA damper that is 30.38 sq.ft and 888 fpm. Does that sound right to anyone? Is my information above bad? My logic is that at the actuator will be oversized to overcome a lack maintainance on the damper. And also, will oversizing have a negative effect on a dampers' mechanical operation?