Hello
Could somebody tell me how to model a DC bus in SKM.
The system i have right now is AC rectified to DC and inverted to AC back again running 10-12 motors.
The inverters are fed from the DC bus, I am trying to find out the short circuit current available at the DC bus also taking the capacitors in the inverters into effect.
I am aware of the industry standard which says that capacitors can be neglected, but in my case i have 42 drives each with 6 caps of 5600 micro farad. I believe this would make difference to the short circuit at the DC bus. I cannot find a way to model this stuff. I have also attached a picture of the setup
Any help would be appreciated.
Thanks!!
Could somebody tell me how to model a DC bus in SKM.
The system i have right now is AC rectified to DC and inverted to AC back again running 10-12 motors.
The inverters are fed from the DC bus, I am trying to find out the short circuit current available at the DC bus also taking the capacitors in the inverters into effect.
I am aware of the industry standard which says that capacitors can be neglected, but in my case i have 42 drives each with 6 caps of 5600 micro farad. I believe this would make difference to the short circuit at the DC bus. I cannot find a way to model this stuff. I have also attached a picture of the setup