Thedroid
Electrical
- May 18, 2008
- 196
2 different drives are experiencing higher than normal bridge temps after a 6 month shutdown. Both are ABB DCS 500's. One is for a 40 hp motor, the other is for 2 75hp with the armatures in series. They are both way under FLA. Before the shutdown these drives both had bridge temps under 30C. Within hours of startup we were seeing temps around 60C. We're using portable ac units right now to keep the temps down to around 35, but would like to remove them at some point. Both drives are supplied by the same 4160/480 delta/wye and they each have their own 480/480 delt/wye isolation transformers. Voltage measurements are 485 l-l and 295 320 295 l-g off the isolation transformer, and normal before it. Is there a common component that may be failing from sitting too long?