edison123
Electrical
- Oct 23, 2002
- 4,462
Our client has a 440 V, 40 HP, 75A, 400 RPM base speed DC Motor driven by Eurotherm 590 + drive with 110 Amps capacity. The motor drives a rubber calendaring mill with a speed ranging from 400 RPM (field current 5.0 Amps) to 700 RPM (field current 2.4 Amps). The armature current as measured by an AC/DC clip on ammeter was found to vary from 20 Amps to 65 Amps. The current limit of the drive has been fixed at 95% of rated 75 Amps by the drive manufacturer’s rep.
This DC drive has tripped many times since its recent installation on “pulse missing”. In the field weakened range of about 650 to 690 RPM, the drive often goes to current-limit, the armature voltage is seen to vary from 200 to 570 Volts, and the field voltage from 70 to 270 volts. The drive indicates a speed error of 1.2 to 1.5%. At lower speeds, the armature and field voltages are stable.
1. What could be causing these trips on “pulse missing” ?
2. Is the current limit of 95% of rated current (as set by the drive rep) correct ? (Wouldn’t 125% be the norm for over current limits ?)
3. Why this hunting of armature and field voltages in the field weakened operation ?
4. The Eurotherm rep has advised to change the existing 4% line reactor to 2% reactor ? Is this ok ?
The same motor was previously working fine with a Siemens drive with 4% line reactor. The motor was also thoroughly checked after this tripping problem and found to be alright in all aspects.