Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

DC motor FLA

Status
Not open for further replies.

StanleySmith

Electrical
Jun 4, 2005
18
0
0
US
hey guys, I'm using a 120/220VAC drive to power a 1/3 HP DC motor. I want to calculate the FLA.
What's the formula??? Can I use this relatioship 1HP =746W =746x1Vx1Amp ?
Thank you,
 
Replies continue below

Recommended for you

"a 120/220VAC drive to power a 1/3 HP DC motor"

How do you mean? Connecting a DC motor to an AC drive? I do not understand.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
It depends on what the rated voltage is. If it is 90 V and we assume 80 % efficiency, then your FLA will be something like 250[W]/90[V]/.80 = 3.5 A. If it is 180 V, you will get half of that current.

Is there an excitation winding as well? If so, is it supplied by a separate rectifier - or do you supply it from the main rectifier. In the latter case, you need to add the field winding current to the total.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
For the DC motor circuit:
I = Pe/V
were:
Pe = electric power supplied in watts = Pot/EFF
V = motor input voltage
Pot = Mechanical Power output in watts
EFF = Motor efficiency
 
Status
Not open for further replies.
Back
Top