hello,
i'm having a hard time figuring out the actual voltage drop of a DC circuit and i think it's due to a bad calculation with the resistance.
amps=70kA
VDC=100
L=450 ft
Conductor is 7.50" o.d x 5.5" i.d. water cooled bus.
sufficient water flow through out circuit on multiple inlet connections.
cross section is 20.42 sq. in.
can someone help me with this?
I can figure out the voltage drop once i get the right resistance of copper for this size bus.
thanks.
R = V/I
You have both V and I.
The other details don't really matter.
Here's an online calculator that can (perhaps) be pressed into service:
Entered 20.42 by 1 inches and 450 feet, and the result was 0.000177 ohms.
You certainly shouldn't trust this result without quadruple checking it in different ways. I suggest this primarily as yet another easy datapoint to add to the mix.
PS: What was the "VDC=100" that you mentioned?
100 v(dc)total output from rect/trans
i need to figure out the total resistance of the conductor across 450 ft. to calculate the total voltage drop of the circuit.
there are are 2 conductors in parallel carrying 70kA @ 100vdc.
i'm having problems figuring the length into the equation.
i know to use r=v/i=.00142, but where do figure in the resistivity of copper of 1.7x10e-8 as the factor? and the length?
The drop should be I*?*len/area
I=70000
?=??? (does this factor include the mat'l? this is where i get confused...i think)
L=450
A=in sq. in? cir mil?
You are driving yourself crazy by insisting on using antique units (how about throwing in a "furlong" just to make things funnier).
Recalculate using meters for length and square meters for cross-section, then the formula given by IRstuff will work using 1.7x10e-8 for p.
Benta.
I just did the manual calculation using the above and it matched the online 'trace resistance calculator' to four digits (higher apparent accuracy than the significant digits of the input variables).
If temperature in cable is about 20C, drop voltage is aprox. 0.146V, or 0.146%.
If I undestood corectly, area A = (pi*7.5^2/4 - pi*5.5^2/4) = 20.41sq.in = 131.67 cm2.
Cooper resistivity at 20C Rcu = 2*10^-8 ohm.m
Lenght l = 2*450ft = 297m
R = Rcu*l/A = 2*10^-8 * 297/131.67/10^-4 = 4.51*10^-4 ohm
DV=R*i=4.51*10^-4 * 70*10^3 = 31.57V... in first calculation I used a wrong cooper resistivity value...
And power lose in cable is Pcu = 2.2MW... sure it's not a real system wuth such power lose.
I had found 12.4 volts (the IR drop) one-way - both from the on-line calculator (I linked above) and by way of handraulic calculation. This matches what IRstuff found.
iop95 is using a slightly different value for ?.
Regarding the 450 feet - I wonder why they don't move the transformer a bit closer. It would pay for itself from the recycled copper, power savings, and waste heat. ;-)
70kA is a little unusual, unless it is a a fault current.
(2B)+(2B)' ?
I think your conductor is a steel [pipe] of 0.1 ohm.mm^2/m resistivity and 0.005 1/degreeC temperature coefficient.The conductor temperature has to be 90 degrees C.
70kA is fully load current 24/7.
Customer shows 3.5v drop.
i used so many different k factors and never got close to 3.5.
maybe i should clarify just in case it's not clear.
2 water cooled conductors running in parallel for a total of 450' (450'/conductor)