Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

DC to AC conversion

Status
Not open for further replies.

petronila

Electrical
Jul 28, 2005
491
Dear All

I am interested in to know about a simple, cheap and good method to convert DC in AC the frequency coul be in a range from 40 to 65 Hz

Thanks for the inputs

Carlos
 
Replies continue below

Recommended for you

Hi petronilla,

What voltage? What power level or current?

Thanks,

Goober Dave
 
Hello Dave
The objective of the system is to convert 600V DC into AC (3~). The power will be 3 Kw.

Thanks

Carlos
 
Standard VFDs usually can do this. Some may have three-phase supervision that doesn't allow direct coupling of DC to the DC link. Others can be parametrized for that.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
Expect that with a 600VDC input, the max output voltage from a VFD will be 400VAC.

As Skogsgura said, many VFDs will do this. Technically they all theoretically are capable but because of differences in where the VFD attains it's control power, some will not function if the AC input is not present. So just check with different manufacturers to be sure by telling them exactly what you plan to do.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> faq731-376
 