de-humidification with a DX coil 1

Status
Not open for further replies.

mechanicaldup

Mechanical
Jun 30, 2005
155
I have an application where the outside design condition is 35°C, 75 % RH.
The room design condition is 22°C, 50 %RH. A relative small amount of outside air is supplied to the room (infiltration)

How do you indicate on the psychrometric cart the de-humidification process? How do you calculate the expected %RH in the room?

thks
 
Replies continue below

Recommended for you

You should determine the humidification load then determine how to handle it such that CFM x .69143 x (grains/lb leaving air - grains/lb entering air) = Btu/hr humidification load
 