A CCPP deaerator operates, in theory, just like all deaerators (direct contact heating of feedwater with steam and venting of non-condesables). By "ancient deaerator" I assume that you are referring to a STANDALONE deaerator whose source of heating steam is from a pressure controlled source. In theory, the two (CCPP vs. "ancient") are the same. But the "ancient" will typically operate at a fixed pressure whereas an Integral Deaerator will often operate at a pressure determined by the LP Steam generation rate. The higher the LP steam rate, the higher the pressure. And as I'm sure you're aware, as you reduce CTG load (or duct firing) in a combined cycle plant with a 2- or 3-pressure level HRSG, the LP steam rate goes up. My point about pegging steam applies to both of these deaerators also - if you're worried about corrosion on the boiler's gas side due to condensation in the cool end, you peg it up. In HRSGs you also have the option for feedwater recirculation as a bonus.
The question in this thread dealt with typical pressure profiles for deaerators vs. boiler load. My post notes that an Integral Deaerator in a CCPP may likely be inversely related to regenerative Rankine power plant unless the Integral DA is pegged to reduce gas side condensation. If the DA is of the "ancient" variety and its steam supply is pressure controlled directly by the operator, then its pressure profile doesn't change with boier load.