Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Deck Knee Brace

Status
Not open for further replies.

dgengineering

Structural
Jul 24, 2023
32
Hello everyone,

I am designing a deck with knee braces. It's designed as a separate structure so there is a gap between the existing house and the deck. Because of this gap knee brace has to be connected to the blocking between deck joists, not to a beam. Please see my sketch to visualize this better.
My question is how to connect blockings to the joists? I don't think we can use toe nails. It has to be either inverted hangers or some other method. I need your advice on this please.

Thank you
 

Attachments

  • deck question.pdf
    19 KB · Views: 44
Replies continue below

Recommended for you

Have you actually calculated the demand in the braces? Use 20% of the deck live load as lateral and see what you get. You may think differently about it.
 
I would be inclined to double up on the blocking (make it thicker) and strap the entire length of the blocking all across the deck - this ties the line of blocking together both for compression and tension where it can act as a proper collector. Then lap the knee braces onto the side of the blocking (not the bottom).
 
Never mind the capacity, the H2.5 clips don't feel like they are right for a knee brace anyway. Those are tested for rafters to top plates.

Knee braces aren't fantastic at cutting down the effective length of a column, but most decks the column isn't really controlling anyway, so you want it there for basic stability not to increase the capacity of the post/column (see Steel Design After College on knee braces if you're into K factor discussions).
 
Last edited:
I would be inclined to double up on the blocking (make it thicker) and strap the entire length of the blocking all across the deck - this ties the line of blocking together both for compression and tension where it can act as a proper collector. Then lap the knee braces onto the side of the blocking (not the bottom).
Yep. I second trying to make the connection to the face of the blocking rather than screwing up into it.
 
Status
Not open for further replies.