Once20036
Structural
- Oct 7, 2008
- 533
I was recently hired by a client to retrofit an existing building to support their equipment. They're using roughly 1/2 the building and the other half will be vacant for the time being. It's an existing structural built in the early 80s, joist & joist girder construction, braced frames, cmu exterior, etc. There are no existing drawings.
The issue is that most of the perimeter girders have significant existing overstresses under code required snow loading.
They're 36' long with a wind column in the middle and support 40' long joists. The "girder" is a W12x14.
Checking it as a simply span, i get 500% overstresses.
The slotted connections on the wind column are all bottomed out, so there's gravity load being transferred into the columns which may or may not have existing foundations. Analyzing it over this center column, its roughly 30% overstressed if you count inflection points as braces, or 200% if you ignore inflection points.
There are also uplift issues for the joists and joist girders along the entire perimeter of the building.
I`m planning on writing a letter to my client and the owner pointing out the issues that I've found, but I`m conflicted as to what that letter should recommend. Obviously, this has the potential to be an issue, however, the building has stood for the past 30 years without failure including last year's record snows. It's tough to say that they need to do anything, but on paper this could end poorly.
I`m tempted to indicate what I've found and strongly recommend they hire someone to evaluate this, as it's outside of my scope.
Has anybody run into something like this before? I`d appreciate any advice, insights, or shared experience.
The issue is that most of the perimeter girders have significant existing overstresses under code required snow loading.
They're 36' long with a wind column in the middle and support 40' long joists. The "girder" is a W12x14.
Checking it as a simply span, i get 500% overstresses.
The slotted connections on the wind column are all bottomed out, so there's gravity load being transferred into the columns which may or may not have existing foundations. Analyzing it over this center column, its roughly 30% overstressed if you count inflection points as braces, or 200% if you ignore inflection points.
There are also uplift issues for the joists and joist girders along the entire perimeter of the building.
I`m planning on writing a letter to my client and the owner pointing out the issues that I've found, but I`m conflicted as to what that letter should recommend. Obviously, this has the potential to be an issue, however, the building has stood for the past 30 years without failure including last year's record snows. It's tough to say that they need to do anything, but on paper this could end poorly.
I`m tempted to indicate what I've found and strongly recommend they hire someone to evaluate this, as it's outside of my scope.
Has anybody run into something like this before? I`d appreciate any advice, insights, or shared experience.