samdamon
Structural
- Jan 4, 2002
- 274
I am considering the use of a proprietary mechanical sleeve-type anchor to resist tension loads. The anchors are to be installed in vertical holes on the underside of an existing concrete flat slab. The tension load will vary from 0.3k to 4.5 k many times during the life of the anchor (the anchor is helping attach mobile medical equipment). The ICC-ESR for this anchor (I am designing under IBC '06) has a note that says the anchor should not be used for situations where there is fatigue or shock loading. Unfortunately it does not define what those are. Spoke to the anchor manufacturer and they were not much help. They could only say that fatigue/shock situations were not investigated during the testing of the anchor. Is there a generally accepted definition of what a fatigue load is, or when a load would be considered a "shock" load?
An App D acceptable alternative to this sleeve anchor is a type of adhesive-attached dowel by the same mfgr, but I am hesitant to use the adhesive because of concerns about loss of adhesive strength in a fire. (I also have concerns about installation quality, but would ask for a proof testing program on every adhesive anchor if in the end they were specified).
An App D acceptable alternative to this sleeve anchor is a type of adhesive-attached dowel by the same mfgr, but I am hesitant to use the adhesive because of concerns about loss of adhesive strength in a fire. (I also have concerns about installation quality, but would ask for a proof testing program on every adhesive anchor if in the end they were specified).