Delaminating Glulam Beam Repair 1

Status
Not open for further replies.

Sam165

Structural
Sep 28, 2020
12
Working on a rehab project of a four story multi-family apartment building. The front balcony beam (running parallel to railing) was water damaged to the point of needing to be replaced. Contractor replaced the beam per my recommendation and I was out there doing a QA this morning. While doing my QA I noticed the perpendicular glulam beam that face hangers onto the replacement beam is delaminating at the bottom plies and has a diagonal crack propagating from the over-fastened replacement hanger. The beam is a 3.5”x9.5” Anthony Power Beam that spans 7’-0”. It is supporting perpendicular top chord bearing floor trusses that span 9’ on either end. Live load is 100psf and dead load is 40psf.

I’m thinking of specifying lag screws that are driven from the bottom of the beam to fasten the plies back together. I’m not too worried about the diagonal crack. To figure out the required spacing of the screws, I calculated the max horizontal shear by determining the max bending stress and resolved that into a force couple. I feel like I need to take only a portion of the bending stress that is being resisted by the bottom plies (delaminating plies) but I wanted to get some input from you on how best to proceed. Thanks in advance!

Left face of beam looking into floor cavity.
CC849E3C-83C4-4A05-BF8C-36A71130794B_xzxhwr.jpg


Left face of beam:

02CB1567-F5B4-4E6A-9F62-25230D1AB4FF_p46cwn.jpg


Right face of beam:

9792AAD1-557E-4581-8743-9FD78F6A519C_tvxdcu.jpg
 
Replies continue below

Recommended for you

dik said:
About 30 years back, in Canada, there was a bunch of delaminations... used to know the reason... but have forgotten...

I remember that too. There was a bit of a panic when the government warned everyone about glulam delamination and suggested inspections be carried out on buildings containing glulam beams. I can't recall too many details, but it had something to do with the Hot Press Method of applying glue. I looked for it in existing buildings, but didn't find anything on any of my projects.