jraef,
132Y230 volts is a standard drive isolation transformer secondary here is the U.S. Depending on how you connect the primary taps you can get 138Y240 or 127Y220 out of it. A standard 12-lead standby generator can also be wired to produce this voltage. You cannot get utility supplied 138Y240 but you can get it as a separately derived system where the customer supplies the transformer or generator.
Actually, UNGROUNDED 3-wire 3-phase has more than its fair share of motor and power electronics damage due to silent or invisible lighting during rainstorms. I have experience with both 277Y480 solidly grounded and 480 volts ungrounded and there is no comparison in the rate of motor damage. I also worked at a small factory complex that had 6 480 volt systems, 1 solidly grounded, 3 definitely ungrounded, 1 where the grounding method was unknown, and 1 padmount transformer that was no longer connected to a service. All of the 277Y480 volt solidly gtounded systems had NO surge arrestors and had zero lighting damage to motors, drives, and soft starts.
I have also figured out that there is a 200 volt to 800 volt gap between the 30 minute voltage withstand rating of a motor and the clamping level of surge arrestors that are UL listed for ungrounded and resistance grounded systems. This means that the surge arrestor WILL NOT protect the motors from a 30 minute Saint Elmo's Fire incident unless bleeder resistors are connected phase to ground. The recommendation of an old Audel electrical book was to connect 1 megOhm 5 Watt resistors from each phase to ground. What you can get are 240,000 Ohm 3 Watt metal film resistors that have a 750 volt peak rating. You would connect these in series strings as follows:
3 resistors 240 volts ungrounded
4 resistors 480 volts ungrounded
5 resistors 600 volts ungrounded
The peak voltage rating of these series strings should coordinate with most surge arrestors.
By the way, when a motor controller is in the off state, the motor circuit downstream of the controller is UNGROUNDED! This means that if you are using PVC conduit, unshielded tray cable or UF cable or service entrance cable or whatever, the motor could suffer static electricity damage during rainstorms if bleeder resistors are not connected to the output of the motor controller and a surge arrestor installed at the motor terminals. This explains how a spare pump motor in a sewage plant can blow up the first of second time that it is needed! Also, I would not depend on the antikick diodes in a variable frequency drives to pass output static charge buildup back to a grounded power source. Theoretically, the drive does pass statice electricity back to a grounded source when energized but would you really want the antikick diodes to be doing that?
Mike Cole