Hello, I have a situation where we have a 4.16kV/480V delta/wye w/ 5A NGR, and we want to step it up to 25kV.
If we had the money and time, I would order a 480/25kV delta/wye (or a 4.16/25kV delta/wye actually)… but all we can find is 480/25kV delta-delta and wye/delta (ie: a step down transformer run in reverse).
On the 25kV delta side we’d put in a zig zag and NGR, but I was hoping to get some feedback on the primary 480V side (wye vs ungrounded wye vs delta).
I’ve read countless threads so far but I can’t seem to figure out which is best.
Thanks