jraef
Electrical
- May 29, 2002
- 11,332
I have never worked outside of North America, but I was under the impression that we are, for the most part, the only ones who use delta power distribution systems, that "everywhere else they use wye (star) distribution"; in quotes because a former boss from England made that statement to me once during a discussion of symmetric vs asymmetric fault current, but I have no other direct knowledge.
This subject comes up a lot for me now because VFD manufacturers tend to have a lot of heartburn with delta power systems; some mfrs provide ways to disconnect any internal ground references but warn of potential dire consequences, others simply put it in their instructions that you cannot use them on delta sources at all and you must add drive isolation transformers ahead of them with a solidly grounded wye secondary. I would like corroboration of that old statement, which I took at face value so many years ago. Are delta power distribution systems common in the IEC based world?
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
This subject comes up a lot for me now because VFD manufacturers tend to have a lot of heartburn with delta power systems; some mfrs provide ways to disconnect any internal ground references but warn of potential dire consequences, others simply put it in their instructions that you cannot use them on delta sources at all and you must add drive isolation transformers ahead of them with a solidly grounded wye secondary. I would like corroboration of that old statement, which I took at face value so many years ago. Are delta power distribution systems common in the IEC based world?
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden