Hello everyone,
I was reviewing through faults on the LV side of a non-standard delta wye transformer connection. My intention was to understand how the HV line currents would flow based on the type of secondary through fault…
The Delta side of the transformer would be connected non-standard ANSI connection with DAC on the HV side. LV side would be connected in Wye with the neutral solidly grounded.
This effectively makes it a Dyn11 transformer connection. Therefore, the secondary reference voltage LEADS the primary reference voltage by 30 degrees. Or in other words, the secondary reference voltage LAGs the primary reference voltage by 330 degrees - hence the non-standard connection. See this YouTube video for this transformer connection: [URL unfurl="true"]https://youtu.be/jwvGStgPANE?list=PLqJ0Y2s60r-5TG3jkbk9Er5OPI50i37kh[/url]
Anyway, as I was searching the internet and found an SKM article (attached) which shows the transformer connection in DAC but the flow of HV line current does not match my analysis. In fact, there are many inconsistencies in the article itself.
I wanted to get some feedback from this forum to ensure that my analysis is the correct way of thinking about it. Apologies for squiggly lines… Made this in a hurry.
Thanks!
I was reviewing through faults on the LV side of a non-standard delta wye transformer connection. My intention was to understand how the HV line currents would flow based on the type of secondary through fault…
The Delta side of the transformer would be connected non-standard ANSI connection with DAC on the HV side. LV side would be connected in Wye with the neutral solidly grounded.
This effectively makes it a Dyn11 transformer connection. Therefore, the secondary reference voltage LEADS the primary reference voltage by 30 degrees. Or in other words, the secondary reference voltage LAGs the primary reference voltage by 330 degrees - hence the non-standard connection. See this YouTube video for this transformer connection: [URL unfurl="true"]https://youtu.be/jwvGStgPANE?list=PLqJ0Y2s60r-5TG3jkbk9Er5OPI50i37kh[/url]
Anyway, as I was searching the internet and found an SKM article (attached) which shows the transformer connection in DAC but the flow of HV line current does not match my analysis. In fact, there are many inconsistencies in the article itself.
I wanted to get some feedback from this forum to ensure that my analysis is the correct way of thinking about it. Apologies for squiggly lines… Made this in a hurry.
Thanks!