Deluge System of Transformers

Status
Not open for further replies.

rajendrarohra1978

Electrical
Jul 16, 2013
19
The Main Power Transformers in the Facility are provided with Deluge Fire Protection system. Is it mandatory to Test & release huge amounts of water on running Transformer. Is there any Standard for Deluge Testing on running transformer

Thanks
 
Replies continue below

Recommended for you

See the requirements of chapter 10 and 11 of NFPA 15. Extra requirements are typically mandated by inssurer bodies (if any) too.
 
I witnessed 100’s of deluge trips on transformers 99.9% of the time the plant was down for annual maintenance thus no power to the unit. Most common problems were clogged sprinklers or failure for the detector to operate resulting in no trip. Key was looking at all heads to ensure they are operating and cover the entire transformer. I was involved as an insurance representative.

 
See FM Global Property Loss Prevention Data Sheets 5-4 Transformers 50 plus pages from an insurance carrier. They are free to download.

 
The unique issues related to main station transformer fire protection and design are contained within this document ..

NFPA 850, Recommended Practice for Fire Protection for Electric Generating Plants and High Voltage Direct Current Converter Stations

Tell us more about your particular transformer, deluge containment design, shielding walls and other details..

Please post pictures ....

MJCronin
Sr. Process Engineer
 