racobb
Electrical
- Feb 23, 2009
- 327
I have been getting info from a customer as follows. They have a unit that is supposed to draw 17 to 18 amps at single phase 480 volts. The facility is served 4 wire 480/277 Y 2500 amp service. Service voltage is about 490 and 480+ at the unit. The current measurement on each of the lines connected to the unit are about 54 and 47 amps consistently. That I do not understand since it is 480 single phase, no neutral. I had them shut down everything in the plant except for the Demag unit and they tell me that the current climbed to about 64 and 56 amps. Don't know how much the voltage climbed, but I am sure it probably did to an extent.
The unit was installed in May 09 and I am told that it worked just fine until about October when it started blowing 50 amp fuses that were installed by the Mfg for this 17 to 18 amp load. Appears that no one ever checked the amps before it began blowing the fuses.
Since October, the unit has been sent back to the factory and checks out ok. The customer also has taken it to another plant and it draws 10 and 23 amps on a single phase 480 connection? They also added a temporary isolation transformer and the amps dropped about 6 to 8 on each leg.
I am told that the amp measurements were taken with a clip on ammeter, but I do not know what type.
We have installed a recorder on the service and will be talking with the Mfg tomorrow.
Am waiting on drawings, but I am told it has a 70 kVAR capacitor and a "demag" coil in parallel internally. If that is correct, I am having some heartburn with the 17 to 18 amps.
Any of you guys have experience with the demag equipment?
Thanks
Alan
The unit was installed in May 09 and I am told that it worked just fine until about October when it started blowing 50 amp fuses that were installed by the Mfg for this 17 to 18 amp load. Appears that no one ever checked the amps before it began blowing the fuses.
Since October, the unit has been sent back to the factory and checks out ok. The customer also has taken it to another plant and it draws 10 and 23 amps on a single phase 480 connection? They also added a temporary isolation transformer and the amps dropped about 6 to 8 on each leg.
I am told that the amp measurements were taken with a clip on ammeter, but I do not know what type.
We have installed a recorder on the service and will be talking with the Mfg tomorrow.
Am waiting on drawings, but I am told it has a 70 kVAR capacitor and a "demag" coil in parallel internally. If that is correct, I am having some heartburn with the 17 to 18 amps.
Any of you guys have experience with the demag equipment?
Thanks
Alan