electrageek
Electrical
- Mar 11, 2002
- 116
I am wondering it someone makes a Synchroscope that can be connected to the high and low sides of a Unit Connected Generator. Unit Connected =(Generator is hard wired to the Low-voltage side of the GSU with the Generator Breaker on the High-side of the GSU). The owner would like a Synchroscope but the problem is the Generator is 4160 with (4160:120) PT's WYE connected. The GSU is a 12.47kV High-side with 7200:120 PT's connected in a Wye. So the Synchroscope will have will have 120Vac on the 4160V side and 208V on the 12.47kV side plus a 30deg phase shift due to the Y Delta GSU transformer. The SEL700G relay we have can do the phase and ratio adjustments and provide a synch-check and auto-synch functions but the owner is looking for a Synchroscope that can display the real time phase relationship for the operators. Does anyone make a device like that?