kply_231

Electrical
Apr 4, 2016
18
0
0
CA
Does someone know reference to an international standard like IEEE or IEC that could help in determining the time period that should be used for calculating the demand factor of a motor? Also, does any standard allow applying demand factor to motor FLA's for voltage drop calculations? I am in Canada and the code that I refer is Canadian Electrical Code part 1.
 
Replies continue below

Recommended for you


Demand factors apply to feeders with a diversity of loads.
Demand factors are covered in the Canadian Electrical Code
Section 8- Circuit loading and demand factors section 8-Demand Factors
For individual Motors you want to see Service Factors
See:
Section 28 — Motors and generators
28-010 Special terminology
Service —
Continuous duty service
Non-continuous duty service
— an application of a motor where the apparatus driven by the motor has
the characteristics described in
Section 0, Definitions, under Duty, as Short-time duty, Intermittent
duty, Periodic duty, and Varying duty.


Voltage drop: See Rule 8-102 Voltage drop
Se also:
Table 27 Determining conductor sizes for motors for different requirements of service 352
Appendix B Notes on Rules:
Section 8
Section 28

Bill
--------------------
"Why not the best?"
Jimmy Carter
 