Aikah-Eng
Mechanical
- Nov 27, 2021
- 22
Hi Dears,
I would like to confirm if my fire system design concept and steps are correct or not in this example project that I'm trying to design practice on it,
as a junior designer studying NFPA13 and other codes, I feel many concepts and subsections I understood wrongly!
Please review my question and help me
The project is : Ground+4parking typical floors + 18 residential apartments floors,
all main services rooms located in the ground floor and commercial shops
I have considered the parking 4th floor as the most demanding area for flow rate as it's OH-2 in my local code,
number of 12 sprinklers I've considered in the 1500 sq.ft
and the most remote area required residual pressure in the apartments top most floor 18th, and its LH residential sprinklers,
my concern is do I have to make 2 separate hydraulic calculation for each hazard and consider from both the highest flow and residual pressure required?
in this attached photo is the most remote sprinkler from the pump, upper top right corner , tis in chapter 11 (2016ed) shall be residential special design
approach correct? residential sprinkler in high rise building apartment
I'm going to consider 8 sprinkler head as attached photo in my hydraulic calculation?
I hope u will get what I'm trying to say
there is also automatic wet standpipe, i have 3 risers in this building, any way my pump flow will be 1000 GPM that will serve sprinklers as well
but I want to know if my concept is correct or not?
your answer will be appreciated,
I would like to confirm if my fire system design concept and steps are correct or not in this example project that I'm trying to design practice on it,
as a junior designer studying NFPA13 and other codes, I feel many concepts and subsections I understood wrongly!
Please review my question and help me
The project is : Ground+4parking typical floors + 18 residential apartments floors,
all main services rooms located in the ground floor and commercial shops
I have considered the parking 4th floor as the most demanding area for flow rate as it's OH-2 in my local code,
number of 12 sprinklers I've considered in the 1500 sq.ft
and the most remote area required residual pressure in the apartments top most floor 18th, and its LH residential sprinklers,
my concern is do I have to make 2 separate hydraulic calculation for each hazard and consider from both the highest flow and residual pressure required?
in this attached photo is the most remote sprinkler from the pump, upper top right corner , tis in chapter 11 (2016ed) shall be residential special design
approach correct? residential sprinkler in high rise building apartment
I'm going to consider 8 sprinkler head as attached photo in my hydraulic calculation?
I hope u will get what I'm trying to say
there is also automatic wet standpipe, i have 3 risers in this building, any way my pump flow will be 1000 GPM that will serve sprinklers as well
but I want to know if my concept is correct or not?
your answer will be appreciated,