sl3656
Mechanical
- Sep 14, 2018
- 37
Referring to the design / density curve from NFPA 13, although the selection point along each curve (e.g. LH, OH-1, OH-2, EH-1 and EH-2) is at the discretion of the fire protection designer, I have seen most designers select the lowest area to achieve the lowest mass flow rate upon activation, and therefore the most cost-effective solution.
What rationale would a designer have for moving 'up the curve' to a higher sprinkler operational area? I am in a situation with a client, where he is requesting a specific higher sprinkler activation area, and wants us (the sprinkler designer) to provide engineering analysis to substantiate the higher operational area. I want to avoid a performance-based approach with engineering analysis - is there anything in the various NFPA codes that I could used to counter the client's proposed approach? I'm of the opinion that if NFPA advocated a performance-based approach with sprinkler design, us designers would be charging more hours for each and every design we complete!
What rationale would a designer have for moving 'up the curve' to a higher sprinkler operational area? I am in a situation with a client, where he is requesting a specific higher sprinkler activation area, and wants us (the sprinkler designer) to provide engineering analysis to substantiate the higher operational area. I want to avoid a performance-based approach with engineering analysis - is there anything in the various NFPA codes that I could used to counter the client's proposed approach? I'm of the opinion that if NFPA advocated a performance-based approach with sprinkler design, us designers would be charging more hours for each and every design we complete!