Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

design for shear 4

Status
Not open for further replies.

leitao110

Materials
Oct 27, 2015
4
I want to know what is the difference of these two formulas.On the design of concrete structures book, in the calculation provided concrete shear formula, Vc = 0.17λ√fcbwd. But in the ACI Code 11.2.1, Vc = 2λ√fcbwd. Why do they always will be a difference of nearly 10 times factor.I am a Chinese student of civil engineering in the concrete structure design principle of our books, involved in concrete on shear and tensile strength of concrete is concerned, Vc = 0.7ftbh. Is √fc equivalent tensile strength of concrete.
 
Replies continue below

Recommended for you

My concrete books have shear as Vc = 2λ√fcbwd.
 
Agreed, the difference you notice is probably due to units of the f'c value. The ACI equation starting with 2 expects f'c to be in units of psi. I am not familiar with your equation starting with 0.17, but I suspect it expects f'c in different units (metric, perhaps?). Because the equation relies on the square root of the compressive strength, the units don't work out correctly unless combined with a hidden unit typically buried in that leading coefficient.

Typically, the tensile strength of concrete (we call it the modulus of rupture) is considered proportional to √fc
 
The difference is units: SI vs US customary units. Look at appendix F of ACI 318 for equivalent SI formulas.
 
Status