Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Design of Post embedment in concrete. 1

Status
Not open for further replies.

Lina

Structural
Jul 2, 2001
37
I have seen the following formula for designing post embedment in concrete:

a = (2M^2 + 3LM)/3M + 6L

Do you know where I can find this formula?

Other engineers have used it to calculate embedment of guardrail's posts in concrete.
 
Replies continue below

Recommended for you

Please define the terms used in the equation.
 
Ron.

M = Embedment of guardrail post in cobcrete slab usualy equal to 4"

L = The height of post over finish floor (or slab)
this value should be 42" as per all local codes.

a= distance of first triangular stress below finish floor

after a is obtained other engineers have used it to calculate the force below concrete using this formula

P2= (a^2 x p)/[mx(2a-m)]
Where p is the lateral force on top of the post and as per local codes this force should be 200lb

Thanks for your help.
 
Don't know about your equation but there is a good example in the Steel Designer's Manual 4th Edition published by the Steel Construction Institute. Look under Pocketed Crane Bases.
Regards Andy Machon


 
More details on these formulas:

a= 2 M2 + 3L.M /3M + 6L


P2= a2 x P / [M(2a-M)]

M is the embedment length of the post in the concrete slab
L is the height of the guardrail post
P is the lateral load applied on the top of the post described abve
P2 is the resisting force to P below concrete slab
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor