Hi everyone,
We are designing a 3 story wood portion that sits on one story of concrete; the lateral system is concrete shear walls for the concrete and light frame wood shear walls for the wood portion. Due to the building geometry I need to use the exterior walls as part of the lateral system on the to have at least 3 sides of the diaphragm supported.
Using the NDS Seismic & Wind Provisions 2015, the perforated shear wall method seems pretty simple but it comes with some limitations, one being that the amount of wall above and below the opening is the same. For me, it's 6" off- I am weighing up whether or not to ignore this, but in the meantime I wanted to explore the force transfer around openings method.
I have looked at a number of design examples including a nice spreadsheet produced by the APA, but both the design examples and the spreadsheet only look at one story at a time. The force transfer method derives of all the other forces in the wall including the straps around the windows from the hold down force at the end of the wall. For my lowest story, the cumulative shear in the wall and the hold down force at the end of the wall is obviously much higher. If I analyse this lowest wall I feel like I need to run two scenarios and then somehow join them together:
1) Applied cumulative shear force at the top of the wall to calculate sheathing requirements
2) Applied dummy force to replicate the hold down force at the end of the wall
Doing 2) gives me crazy forces around these openings and it doesn't feel correct. Am I doing this the right way?
As a side note, we had a previous design of this building from another engineer. I checked what they had used to see if I was heading in the right direction, but they had only a couple of typical notes about interior and exterior walls all being sheathed in gypsum with minimal connections and hold downs. I understand the code allows this to resist forces but their drawings just seemed remarkably light...
Thanks.
We are designing a 3 story wood portion that sits on one story of concrete; the lateral system is concrete shear walls for the concrete and light frame wood shear walls for the wood portion. Due to the building geometry I need to use the exterior walls as part of the lateral system on the to have at least 3 sides of the diaphragm supported.
Using the NDS Seismic & Wind Provisions 2015, the perforated shear wall method seems pretty simple but it comes with some limitations, one being that the amount of wall above and below the opening is the same. For me, it's 6" off- I am weighing up whether or not to ignore this, but in the meantime I wanted to explore the force transfer around openings method.
I have looked at a number of design examples including a nice spreadsheet produced by the APA, but both the design examples and the spreadsheet only look at one story at a time. The force transfer method derives of all the other forces in the wall including the straps around the windows from the hold down force at the end of the wall. For my lowest story, the cumulative shear in the wall and the hold down force at the end of the wall is obviously much higher. If I analyse this lowest wall I feel like I need to run two scenarios and then somehow join them together:
1) Applied cumulative shear force at the top of the wall to calculate sheathing requirements
2) Applied dummy force to replicate the hold down force at the end of the wall
Doing 2) gives me crazy forces around these openings and it doesn't feel correct. Am I doing this the right way?
As a side note, we had a previous design of this building from another engineer. I checked what they had used to see if I was heading in the right direction, but they had only a couple of typical notes about interior and exterior walls all being sheathed in gypsum with minimal connections and hold downs. I understand the code allows this to resist forces but their drawings just seemed remarkably light...
Thanks.