You need to work out where your vent and drain system then has no chance of blockage or accidental valve isolation until it reaches the atmosphere. If there is any chance of this then your vent and drain pipework needs to be rated to the same as your vessel regardless of what isolation you have from your vessel / boiler. Assuming you can assure yourself that it won't see full vessel / boiler poressure then you need to work out the maximum pressure in the vent/drain assuming that you open all the isolation valves fully and the boiler is discharging at max rate to atmosphere via your vent OR drain. This can be quite a high pressure, but you cannot assume, in design, that the operator will only slowly open the valve or use the throttling valve correctly. I have often seen an RO in place to limit flow into a drain or vent for this exact purpose (avoid huge flows which overpressure the drain/vent), especially for gas and steam.
This is often a key item when you HAZOP the system and needs to be looked at carefully as early as posisble as the design pressure and temeprature of vents and drains is often very low compared to the boiler. Getting it wrong is frequently a cause of failure and incident when a vent or drain is over pressuriseid and ruptures or is exposed to much lower or higheer temperatures than design. Just becasue it's "the vent" or "the drain", doesn't mean you can ignore the potential for over pressure. Equally having to change it later in the design is also a real pain.