Hi,
I have a question about using stainless steel jacketed mineral wool versus calcium silicate for fire protection of a process vessel. API 521 section 4.4.13.2.7.2 says that stainless steel jacketing and banding have demonstrated satisfactory performance in fire situations. A number of the threads on this site talk about using mineral wool that has been jacketed and banded with stainless steel for fire protection.
There is a 9000 litre process vessel, which cannot be realistically protected against two phase flow in the fire case, in part because it vents at very high level, above roof level, and because its worst case reactant has a very low latent heat per mole. There is a preference to have a pressure safety valve in the emergency vent rather than just a bursting disc, which also limits relief rates unless you install a relief valve the size of Kilamonjaro and then some poor shmuck has to remove it down to the workshop for testing once a year. My company will not want to reduce the level in the vessel a lot because that would reduce the throughput that is available from that vessel. Avoiding the risk of fire entirely does not seem to be an option either since there is hot oil and boiling flammable reactants present.
The obvious solution is to make use of a low environmental factor, to limit the amount of heat that can go into the vessel in the event of a fire. In order to maintain full usage of the vessel, it would be necessary to achieve an environmental factor of 0.15. I would aim for an environmental factor of 0.1 or better to be sure, and then go slightly over the top on the insulation/cladding reliability. I am aware that some design houses will not use an environmental factor less than 0.3 because they say that it is difficult to be sure that insulation will all stay on in the event of a fire, whereas others have no such rule, and the codes do permit the use of an environmental factor less than 0.3. A safety advisor from a previous company told me that you couldn’t rely on stainless steel cladding not to warp, buckle and fall off at the high temperatures in a fire, although this does not seem to chime with API 521. My company is a small one with just one site with old vessels from the 1960s and will want to do things well and professionally and economically. Can anyone offer any advice on how to go about designing insulation / cladding to make it reliably fire-proof without breaking the bank, or recommend a book? Alternatively, tell me why API521 is demonstrably wrong and stainless steel clad mineral wool cannot reliably resist a fire.
We also have some vessels with limpet coils that need occasional repair welds. I have no idea how to deal with those because it seems impossible to provide fire proof lagging that can easily be removed for maintenance inspection. The best plan I’ve managed so far involves throwing them away and starting with new vessels, so any views on those would also be welcome.
Thank you!
I have a question about using stainless steel jacketed mineral wool versus calcium silicate for fire protection of a process vessel. API 521 section 4.4.13.2.7.2 says that stainless steel jacketing and banding have demonstrated satisfactory performance in fire situations. A number of the threads on this site talk about using mineral wool that has been jacketed and banded with stainless steel for fire protection.
There is a 9000 litre process vessel, which cannot be realistically protected against two phase flow in the fire case, in part because it vents at very high level, above roof level, and because its worst case reactant has a very low latent heat per mole. There is a preference to have a pressure safety valve in the emergency vent rather than just a bursting disc, which also limits relief rates unless you install a relief valve the size of Kilamonjaro and then some poor shmuck has to remove it down to the workshop for testing once a year. My company will not want to reduce the level in the vessel a lot because that would reduce the throughput that is available from that vessel. Avoiding the risk of fire entirely does not seem to be an option either since there is hot oil and boiling flammable reactants present.
The obvious solution is to make use of a low environmental factor, to limit the amount of heat that can go into the vessel in the event of a fire. In order to maintain full usage of the vessel, it would be necessary to achieve an environmental factor of 0.15. I would aim for an environmental factor of 0.1 or better to be sure, and then go slightly over the top on the insulation/cladding reliability. I am aware that some design houses will not use an environmental factor less than 0.3 because they say that it is difficult to be sure that insulation will all stay on in the event of a fire, whereas others have no such rule, and the codes do permit the use of an environmental factor less than 0.3. A safety advisor from a previous company told me that you couldn’t rely on stainless steel cladding not to warp, buckle and fall off at the high temperatures in a fire, although this does not seem to chime with API 521. My company is a small one with just one site with old vessels from the 1960s and will want to do things well and professionally and economically. Can anyone offer any advice on how to go about designing insulation / cladding to make it reliably fire-proof without breaking the bank, or recommend a book? Alternatively, tell me why API521 is demonstrably wrong and stainless steel clad mineral wool cannot reliably resist a fire.
We also have some vessels with limpet coils that need occasional repair welds. I have no idea how to deal with those because it seems impossible to provide fire proof lagging that can easily be removed for maintenance inspection. The best plan I’ve managed so far involves throwing them away and starting with new vessels, so any views on those would also be welcome.
Thank you!