elyengineering
Structural
- Nov 5, 2005
- 9
Have read through previous threads regarding C&C vs. MWFRS forces.
Am designing connections for residential trusses in a 150 mph wind zone. Two-story, wood-framed residence. I don't typically design in high wind area, so am less familiar with the typical detailing.
According to my calcs, with uplift of over 1,000# at the ends of trusses, this would necessitate strapping studs at all such locations continuously from roof to foundation.
Does this sound consistent with typical Florida design?
I'm in California, and in lesser wind ares, typically just carry uplift from shear wall/hold down forces continuously to the foundation.
This seems like a lot of studs to strap, but perhaps is the way it's done.