A client asked us to verify that a structure of theirs (i.e., down to/including its individual components) meets a safety factor of 5:1.
To summarize my calculation for FoS:
I calculate the design strength (?Rn for LRFD (?=0.75), Rn/? for ASD (?=2)) then divide that by the actual force, P being applied to the member to determine the FoS.
For example:
LL = 10 kips
DL = 10 kips
Rn = 120 kips
LRFD
------
P = 1.2(10) + 1.6(10) = 28 kips
?Rn = 90 kips
FoS = 90/28 = 3.21
CHECK: FoS > 5 - NO!
ASD
------
P = D + L = 20 kips
Rn/? = 60 kips
FoS = 60/20 = 3.00
CHECK: FoS > 5 - NO!
Is this calculation correct? Or am I adding a safety factor to a safety factor?
For example, should the calculation be this:
Rn = 120 kips
P = 20 kips
FoS = Rn/P = 6
CHECK: FoS > 5 - YES!
Please help! And provide any support documents (posting .pdfs, .jpgs, etc.) or document citations if possible.
Thanks!
To summarize my calculation for FoS:
I calculate the design strength (?Rn for LRFD (?=0.75), Rn/? for ASD (?=2)) then divide that by the actual force, P being applied to the member to determine the FoS.
For example:
LL = 10 kips
DL = 10 kips
Rn = 120 kips
LRFD
------
P = 1.2(10) + 1.6(10) = 28 kips
?Rn = 90 kips
FoS = 90/28 = 3.21
CHECK: FoS > 5 - NO!
ASD
------
P = D + L = 20 kips
Rn/? = 60 kips
FoS = 60/20 = 3.00
CHECK: FoS > 5 - NO!
Is this calculation correct? Or am I adding a safety factor to a safety factor?
For example, should the calculation be this:
Rn = 120 kips
P = 20 kips
FoS = Rn/P = 6
CHECK: FoS > 5 - YES!
Please help! And provide any support documents (posting .pdfs, .jpgs, etc.) or document citations if possible.
Thanks!