I have one house that I am hooking up to a sanitary sewer main 200 feet away via an 8" HDPE pipe, therefore pipe not flowing full. How do I calculate what pipe slope is necessary to flow successfully?
 
Replies continue below

Recommended for you

Are you using an 8" pipe for the service? unless you have a 5 bathroom house that is way over sized. cut back to a max of 6" and even check out a 4". the slope will be the diff. in elev. from the house outlet and the elevation of the main where you hook up divided by the 200 feet to the main. Has nothing to do with half full or full
 
The standard in my area is 6" Dia. pipe at a slope of 1/8" per foot (these are minimums for size and slope). This provides a flow capacity of 1.2 cfs and a velocity of 3.5 fps, flowing full, calculated with Manning's equation.
 