Slightly different type question.
Church Service Size Question
-------------------------------------------
We are doing a church and several of us have a “discussion” going relative to the service size. The loads are as follows:
LOAD KVA Connected "Estimated" KVA Demand
Lights 43 43
Rcpts 61 25
HVAC 320 250
EWH 8 8
Ranges (2) 16 16
RV hookups (3) 18 12
=========================================
466 KVAc 354 KVAd
1305 Ac 991 Ad
Thus provide a 1000A service. (?)
The HVAC's are heat pumps. We used for demans 100% of the heat pumps and 65% for the AHU's (strip heat). Frankly, I think that's on the high size, IMHO.
The code doesn’t specifically help for this type occupancy. We used various pieces of the code to come up with the estimated demands above. Based on experience, they are “reasonable.” Heat pumps are used. The ranges are part of a "warming" kitchen.
It's just under 15,000 ft sq. The sanctuary takes 21 kw of the light load. Plus, I generally round up when sizing lighting circuits.
The sanctuary is on the "bright" side and it does have a dimmer system.
It also has church offices, nursery, class rooms for all ages, a warming kitchen, a kitchenette, etc.
Proposed service would be an I-Line 1200A panel with outside disconnect sized at 1000A. There is additional "discussion" to make the service 1200A. The downside is that two doors would then be required in the room where the 1200A pnlbd is located, but doable, just a PIA.
Anything larger than 1200A bumps cost way up as we need to go to a switchboard. Even splitting things up into two I-Line panels adds to the cost.
As you can imagine, there’s a significant cost difference involved in the two service sizes. We obviously want to provide an adequate service but also don't want to tack on un-necessary costs.
Comments?
What have you used as a guide to determine service size for an occupancy as this?
Thanks in advance.
Church Service Size Question
-------------------------------------------
We are doing a church and several of us have a “discussion” going relative to the service size. The loads are as follows:
LOAD KVA Connected "Estimated" KVA Demand
Lights 43 43
Rcpts 61 25
HVAC 320 250
EWH 8 8
Ranges (2) 16 16
RV hookups (3) 18 12
=========================================
466 KVAc 354 KVAd
1305 Ac 991 Ad
Thus provide a 1000A service. (?)
The HVAC's are heat pumps. We used for demans 100% of the heat pumps and 65% for the AHU's (strip heat). Frankly, I think that's on the high size, IMHO.
The code doesn’t specifically help for this type occupancy. We used various pieces of the code to come up with the estimated demands above. Based on experience, they are “reasonable.” Heat pumps are used. The ranges are part of a "warming" kitchen.
It's just under 15,000 ft sq. The sanctuary takes 21 kw of the light load. Plus, I generally round up when sizing lighting circuits.
The sanctuary is on the "bright" side and it does have a dimmer system.
It also has church offices, nursery, class rooms for all ages, a warming kitchen, a kitchenette, etc.
Proposed service would be an I-Line 1200A panel with outside disconnect sized at 1000A. There is additional "discussion" to make the service 1200A. The downside is that two doors would then be required in the room where the 1200A pnlbd is located, but doable, just a PIA.
Anything larger than 1200A bumps cost way up as we need to go to a switchboard. Even splitting things up into two I-Line panels adds to the cost.
As you can imagine, there’s a significant cost difference involved in the two service sizes. We obviously want to provide an adequate service but also don't want to tack on un-necessary costs.
Comments?
What have you used as a guide to determine service size for an occupancy as this?
Thanks in advance.