Hi everyone. In the attached I've shown 3 details I'm using to try to determine the allowable wind loads for a wall stiffener in a log home. In this case the post isn't long enough to go from floor to roof. After studying it I feel that I should:
A: Consider the reduced section a cantilever, fixed where it meets the full section, to find it's max load based on max bending, shear and deflection.
B: Use single shear, in the reduced section, at the opposite end of the full section to determine the max load that the through bolts and lumber can withstand.
C: Use the smallest load of the two.
To me these seem to be the controlling factors. In this case I do not want to include the force resistance of the logs simply because I want to understand how the load is traveling through the splice in the post. I referenced the logs only to introduce a tributary load to the post.
I guess my question is, am I on the right track with my determinations?
Thanks,
Doug
A: Consider the reduced section a cantilever, fixed where it meets the full section, to find it's max load based on max bending, shear and deflection.
B: Use single shear, in the reduced section, at the opposite end of the full section to determine the max load that the through bolts and lumber can withstand.
C: Use the smallest load of the two.
To me these seem to be the controlling factors. In this case I do not want to include the force resistance of the logs simply because I want to understand how the load is traveling through the splice in the post. I referenced the logs only to introduce a tributary load to the post.
I guess my question is, am I on the right track with my determinations?