bdn2004
Electrical
- Jan 27, 2007
- 792
I'm asked to determine the SCCR of what's been deemed an "Industrial Control Panel" and must meet the qualifications of NEC 409. I understand to use the "weakest link method" UL508A to do this. But in NEC 409 there is this exception to 409.110 (4): "Short-circuit current ratings are not required for industrial control panels containing only control circuit components".
My question then is this:
The box I'm looking at is a custom built heat tracing panel. It has contactors and a panelboard that's connected to the heat tracing circuits. And it has bunch of 120VAC hard-wired control relays that interact with the external thermostats, the pushbuttons, indicating lights, etc and the contactors that power the heat trace circuits.
If this were just a control panel - no rating is needed. Can I assume then that the 120VAC control portion of this panel is ok and doesn't figure into the "weakest link" ?
My question then is this:
The box I'm looking at is a custom built heat tracing panel. It has contactors and a panelboard that's connected to the heat tracing circuits. And it has bunch of 120VAC hard-wired control relays that interact with the external thermostats, the pushbuttons, indicating lights, etc and the contactors that power the heat trace circuits.
If this were just a control panel - no rating is needed. Can I assume then that the 120VAC control portion of this panel is ok and doesn't figure into the "weakest link" ?