bumbler
Structural
- Apr 15, 2022
- 20
Hi all,
In ACI318-14 Table 25.4.2.2, "clear cover at least db" is required to avoid using the more conservative development length equations. Without this clear cover, the equations yield a 50% higher development length. Does this apply at a construction joint? For example, at a concrete wall over a grade beam/footing, are we required to offset a vertical wall bar that is lapping with a vertical dowel to provide cover to the construction joint? We had a contractor request to use dowels from the grade beams and lap vertically. See attached sketch for details.
Thanks!
In ACI318-14 Table 25.4.2.2, "clear cover at least db" is required to avoid using the more conservative development length equations. Without this clear cover, the equations yield a 50% higher development length. Does this apply at a construction joint? For example, at a concrete wall over a grade beam/footing, are we required to offset a vertical wall bar that is lapping with a vertical dowel to provide cover to the construction joint? We had a contractor request to use dowels from the grade beams and lap vertically. See attached sketch for details.