How do your firms show development length and lap splice schedules on construction drawings?
Do you have the most conservative value calculated prior to the modifiers applied and spell out how the modifiers apply? For example, a #5 bar in 5000 psi concrete has a hook development length of 15" but if spaced > 6db and adequate side cover, this value can be reduced to 7.5". So, what value would your tables show?
As a firm, we have opted to show the most conservative length and apply the modifiers to check if hooks develop in a member, but the table values look stupid at first blush for 318-19 (i.e., longer than the member thickness). It does look like sanity will return when 318-25 gets adopted.
Do you have the most conservative value calculated prior to the modifiers applied and spell out how the modifiers apply? For example, a #5 bar in 5000 psi concrete has a hook development length of 15" but if spaced > 6db and adequate side cover, this value can be reduced to 7.5". So, what value would your tables show?
As a firm, we have opted to show the most conservative length and apply the modifiers to check if hooks develop in a member, but the table values look stupid at first blush for 318-19 (i.e., longer than the member thickness). It does look like sanity will return when 318-25 gets adopted.