I have following loads to be connected with a 415V, 50hZ, 3 Ph. Diesel Engine driven Generator:
1) 2 nos. 110kW Induction Motor with DOL starter,
2) 1 no. 22 kW Induction Motor with DOL starter,
3) 1 no. 18.5 kW Induction Motor with DOL starter,
4) 1 no. 15 kW Induction Motor with DOL starter,
5) 1 no. 15 kVA UPS,
6) 10kW Battery Charger for DC Load and
7) 50kW Lighting Load.
The criteria shall be that the largest load (110kW motor) shall be able to start while the rest of the loads are ON. please note that the permissible voltage dip is 15%.
Can anyone help me finalise the kVA rating of the DG Set?? May please assume standard values for calculation.