immsk
Mechanical
- Jul 9, 2012
- 45
Hi,
Two questions:
Easy one first: Do you have a recommendation for a DHW heater sizing resource?
Second question: I am trying to determine the capacity for an existing Domestic hot water system.
I've been reviewing articles and literature to determine the actual capacity of usable hot water in a storage tank. Most sources say 70% to 80% of a tanks volume is usable - two examples below:
1. 80% according to AO Smith here
2. 70% to 80% here by Aerco Link here
I am trying to understand how this 70% to 80% number is determined.
Here are my assumptions:
1. Storage tank size: 100 Gallons
2. Hot water storage temperature: 140F
3. Cold water supply temperature: 40F
4. Lowest acceptable temperature in the tank during use: 110F
5. Assume there is no internal/external source of heating
6. No storage losses
So starting with 100 Gallons of water stored at 140F, I start drawing hot water from the tank. Whatever water I draw is replaced with an equivalent amount of cold water. Based on the image above once 30% of the volume of hot water in the tank is used and replaced with cold water, the tank temperature drops below 110F. Things I have considered:
[ul]
[li]When we initially start with 140F, the water drawn from the tank will be mixed with cold water to supply the fixtures at 120F - so we will be able to produce more usable hot water than is drawn from the tank. However I don't think accounting for this mixing will get me much closer to the 70%-80% range.[/li]
[li] There is stratification within the tank - therefore as cold water enters the hot water tank, it doesn't fully mix - the hot water within the tank stays hotter than a fully mixed tank would - not sure if this is accurate or how much of an impact this has
[/li]
[/ul]
If any one has any ideas on how this 70% to 80% number is determined feel free to chime in.
Two questions:
Easy one first: Do you have a recommendation for a DHW heater sizing resource?
Second question: I am trying to determine the capacity for an existing Domestic hot water system.
I've been reviewing articles and literature to determine the actual capacity of usable hot water in a storage tank. Most sources say 70% to 80% of a tanks volume is usable - two examples below:
1. 80% according to AO Smith here
2. 70% to 80% here by Aerco Link here
I am trying to understand how this 70% to 80% number is determined.
Here are my assumptions:
1. Storage tank size: 100 Gallons
2. Hot water storage temperature: 140F
3. Cold water supply temperature: 40F
4. Lowest acceptable temperature in the tank during use: 110F
5. Assume there is no internal/external source of heating
6. No storage losses
So starting with 100 Gallons of water stored at 140F, I start drawing hot water from the tank. Whatever water I draw is replaced with an equivalent amount of cold water. Based on the image above once 30% of the volume of hot water in the tank is used and replaced with cold water, the tank temperature drops below 110F. Things I have considered:
[ul]
[li]When we initially start with 140F, the water drawn from the tank will be mixed with cold water to supply the fixtures at 120F - so we will be able to produce more usable hot water than is drawn from the tank. However I don't think accounting for this mixing will get me much closer to the 70%-80% range.[/li]
[li] There is stratification within the tank - therefore as cold water enters the hot water tank, it doesn't fully mix - the hot water within the tank stays hotter than a fully mixed tank would - not sure if this is accurate or how much of an impact this has
[/li]
[/ul]
If any one has any ideas on how this 70% to 80% number is determined feel free to chime in.