I am going to rectify 24v to supply a 24VDC motor with an FLA of 57A. The startup current for the motor is around 120A I'm a little confused on how to calculate the inrush capability the rectifier would need to be able to handle.
The spec sheet I have on the diode module (Crydom M50 series) I'm looking at says
di/dt =
"Critical Rate of Rise of On-State @ TJ=125 C (A/uS)" = 100
Additionally, it says that the
"Maximum Non-Repetitive Surge Current (A) [1/2 cycle, 60Hz]"
is 800 for the 60A module and 1500 for the 100A module.
So for a motor pulling roughly 120A at startup, a 60A rectifier should have no problem at all with it....