EnergyProfessional
Mechanical
- Jan 20, 2010
- 1,279
I've searched multiple threads in these forum and still don't know if i should use di-electric unions. I understand the issue of galvanic corrosion, and also understand that if I have an open or domestic water system I introduce new oxygen all the time (I know galvanic corrosion doesn't need that oxygen), and also that it depends on pH value. i know this has been discussed before, but there still is no conlcusion beyond that the theory says they are needed, and the fieldstaff says they are evil ![[pipe] [pipe] [pipe]](/data/assets/smilies/pipe.gif)
but I'm more looking for advice on closed loop HVAC piping with copper/steel pipes. I know theory (and code) prescribe di-electric unions. but I talked to many contractors and also to our maintenance crew and all said:
[ul]
[li]they never saw a corroded pipe where copper/steel met (at least not to the point of failure beyond some light surface corrosion)[/li]
[li]they have seen many di-electric unions leak[/li]
[li]many devices with internal copper / steel transition don't have di-electric unions from the factory[/li]
[/ul]
Obviously this makes me think I would spend money on something that would make systems worse. I usually include a good air removal device, and we use annual chemical treatment. I wouldn't mind spending the money on di-electric unions, that is not the issue, but they seem to bring more problems than they promise to heal. They seem to be something someone sitting in a desk likes, but someone maintaining systems hates them.
Should I look for adding di-electric unions/ and if so, what brands would be good? I believe the issue with leaking di-electric unions also is related to the cheapness.
thanks for any insight.
![[pipe] [pipe] [pipe]](/data/assets/smilies/pipe.gif)
but I'm more looking for advice on closed loop HVAC piping with copper/steel pipes. I know theory (and code) prescribe di-electric unions. but I talked to many contractors and also to our maintenance crew and all said:
[ul]
[li]they never saw a corroded pipe where copper/steel met (at least not to the point of failure beyond some light surface corrosion)[/li]
[li]they have seen many di-electric unions leak[/li]
[li]many devices with internal copper / steel transition don't have di-electric unions from the factory[/li]
[/ul]
Obviously this makes me think I would spend money on something that would make systems worse. I usually include a good air removal device, and we use annual chemical treatment. I wouldn't mind spending the money on di-electric unions, that is not the issue, but they seem to bring more problems than they promise to heal. They seem to be something someone sitting in a desk likes, but someone maintaining systems hates them.
![[sadeyes] [sadeyes] [sadeyes]](/data/assets/smilies/sadeyes.gif)
Should I look for adding di-electric unions/ and if so, what brands would be good? I believe the issue with leaking di-electric unions also is related to the cheapness.
thanks for any insight.