masterdesign
Structural
- Nov 3, 2023
- 22
Consider:
Diaphragm capacity
2021 SDPWS Table 4.2c
Wood sheathing
10d common nails (0.148" x 3")
1 1/2" framing penetration
19/32" sheathing thickness
2" nominal framing (G = 0.50)
6" boundary nailing
Case 1 = 800/2 = 400plf
Case 3 = 600/2 = 300plf
Boundary nailing capacity
10d common (0.148" x 3")
19/32" sheathing thickness (G = 0.50)
1 1/2" framing penetration (G = 0.50)
Z = 95# (2018 NDS Table 12Q or dowel equations)
Z' @ 6" = 95*1.6*12/6 = 304plf
Now I can understand if the diaphragm capacity is less than the design value of the boundary nailing, but how can the diaphragm capacity be more than what the nails can transfer?