In the roof diaphragm, as shown in the below detail, what is the need for this tie 3/8" plate? if there is a beam on both sides of the grid along this diaphragm line (J) and this line has a vertical brace frame positioned, could this 3/8" tie plate detail eliminated?
1744749354750.png
 
Replies continue below

Recommended for you

I would expect that the purpose of the tie plate is to axially splice beams forming part of the collector / chord system on either side of the column.
 
But then, the beams are connected to the column, and then they maintain the continuity for the collector/ chord system right? via shear tabs or however, the beam column connection is
 
The beam connections to the column would have to be designed for both the vertical shear load as well as the horizontal tie load - which the original designer perhaps didn't do - instead separating the function of both entities to "do their own thing".

The vertical shear beam connections probably have some inherent "give" with short horizontal slotted holes perhaps letting the tie plate do all the horizontal work without any load sharing.
 
Thats where I was going to, when the beam-column connection is designed for shear as well as axial loads, it should be fine.

However, I was playing with Ram connections and in the program for this particular case, where there are beam on both sides of the column the program doesn't consider both the beams when designing for the axial load, and the connection fails because of the web of the column (Beam to wide flange column web). The other design checks passed except that the column web failed. In this case, if there is a beam on the other side of the column, then this failure on the column web shouldn't occur right?
 
In this case, if there is a beam on the other side of the column, then this failure on the column web shouldn't occur right?

Sounds about right. I assume that we're speaking of a wide flange column and not an HSS column.
 
Yes its a wide flange column, the detail shows HSS (from other project)
 
You should be good then. The only EOR hang-up that I can envision, potentially, is concern for rotational ductility in the beam to column connection. You will often loose that when that connection is designed for axial load transfer. But, then, you often lose it regardless to some degree so I've not been inclined to lose much sleep over it.
 
The tie plate is presumably there to transfer the load in the beam flange across the connection, rather than forcing it down into the web. Much more efficient if there is significant bending moment in the beam at the connection.
Why would you want to delete the plate?
 
SWComposites: it becomes an additional site work and if it can be avoidable trying to ensure it is ok to avoid
 
if there is a beam on both sides of the grid along this diaphragm line (J) and this line has a vertical brace frame positioned, could this 3/8" tie plate detail eliminated?
The 3/8 tie plate is there specifically because it is in line with a braced frame. I.e., a collector.

PL 3/8x4 Gr. 50 (for a small-ish beam) is good for about 50k ASD. That will hammer a bolt group for smaller beams. Even with bigger beams you'll end up with several columns of bolts in the bolt groups.
You'll see this connection more frequently in roofs framed with bar joists. Specifically subdiaphragms in tilt-up warehouses in earthquake country. In the case of bar joists, there is no other connection to rely on really. You don't want to rip the joist girders' top chords apart out of plane with the transfer load.

In your case with WF beams, the other options are:
1. fully welded shear tabs/clip angles
2. slip critical bolted shear tabs
3. bolted then fully welded shear tabs, which is kindof belt and suspenders and saying "bolts take gravity and welds take axial" (yeah it's more complicated than that but that's the typical explanation of how it works)
4. any combination of the above but with knife plates if it's a HSS column

As you've noted, it is very common to have fabricators and erectors ask for a bolted alternative to these drag connections. Especially on those bigger jobs ;)
 