scott88
Electrical
- Apr 25, 2012
- 16
Hi,
We have a problem with our emergency diesel generator. The generator is a 1100kVA 400V 50 hz machine, manufacturer Leroy Somer with Siemens SIPROTEC 7UM62 relay protecton. On running the generator up it is stable and running fine for anything onload between 40minutes to an hour and then trips on differential protection. The generator has CTs on each phase situated just before the circuit breaker and before the star point. We have tested the generator windings and all are balanced and low, mega checked to earth and between phases all with readings in the Gohms, the CTs have been checked and tested and are also fine.
The readings are.
SIDE 1 (just before the circuit breaker)
L1 - 1.01kA
L2 - 1.02kA
L3 - 1.02kA
SIDE 2 (Just before the star point)
L1 - 0.72kA
L2 - 1.02kA
L3 - 1.02kA
Does anybody have any ideas or advise for further tests or fault interogation?
All other protecion functions are fine and show know pickups or cause for concern.
Thanks,
Scott
We have a problem with our emergency diesel generator. The generator is a 1100kVA 400V 50 hz machine, manufacturer Leroy Somer with Siemens SIPROTEC 7UM62 relay protecton. On running the generator up it is stable and running fine for anything onload between 40minutes to an hour and then trips on differential protection. The generator has CTs on each phase situated just before the circuit breaker and before the star point. We have tested the generator windings and all are balanced and low, mega checked to earth and between phases all with readings in the Gohms, the CTs have been checked and tested and are also fine.
The readings are.
SIDE 1 (just before the circuit breaker)
L1 - 1.01kA
L2 - 1.02kA
L3 - 1.02kA
SIDE 2 (Just before the star point)
L1 - 0.72kA
L2 - 1.02kA
L3 - 1.02kA
Does anybody have any ideas or advise for further tests or fault interogation?
All other protecion functions are fine and show know pickups or cause for concern.
Thanks,
Scott