You can stay Scotty. Under Frequency Roll Off and volt/hertz limiter are similar enough to not matter. On the small machines the UFRO gets a lot more use than the volt/hertz limiter on the big ones.
Wayne, Under Funded, Really Optimistic really gives Under Frequency Roll Off a run for it's money.
You are always welcome David. That is an interesting suggestion.
The quick answer is yes it will work. A more accurate answer may be, I don't know.
If I may share an anecdote that may have some relevance;
I was on a project years ago when forbidden frequencies for pump drives were not well understood. We had some 60 HP centrifugal pumps with VFDs under PID control. At one particular speed setting, the pressure pulse reflections from the first 90, about 50 feet away coincided with the impellor vane period and the pressure pulses started to reinforce. The end result was a piece of casting about the size of my hand being blown out of the pump body. Twice. Lesson learned about forbidden frequencies.
What has that to do with generators? There may be a combinations of motor speeds and or loadings that causes the non-linear current draw of VFDs to reinforce with a bad interaction with the AVR.
I don't know, but were I faced with the installation that you suggest, I would tread cautiously.
Good question!!
Bill
--------------------